John Kloehr Posted December 20, 2020 Share Posted December 20, 2020 First time I've been stumped in decades. Only experienced electricians need read beyond this point. Was vacuuming out rats nests out of the cars outside, house breaker for that circuit blew. Reset breaker, finished job. Turned shop vacuum off. A few minutes later, breaker blew again. Tried to reset breaker, instant pop. Unplugged (I thought) all lamps and such on the circuit (kitty heated bed too). Still an instant pop. Verify power is off, check with ohm meter. 12 ohms from hot to neutral on this circuit... That would be 10amps draw. Find one more lamp plugged in (old-style filament bulb, resistance drops as they heat up, but should not blow breaker). Unplug that. Resistance to neutral (and to ground) is now 0.38 megohm (380,000 ohms). Also found a UPS was activated, one more plug, unplugged that and a lamp (off) too. Also unplugged neon lamp in a bathroom. Breaker still pops instantly. Bad breaker? Disconnect the wire from that breaker and another circuit, try the suspect wire on the alternate breaker. Pops instantly. Also verified neutral is bonded to ground at the panel. So, not a bad breaker, no short circuit, but acts like a short circuit. It is not a GFCI or arc fault breaker, just an old school breaker that will trip on too many amps. But the ohmmeter shows no short. Thoughts? Ohm meter reading says the circuit should draw less than a milliamp, breaker blows like a dead short. And yes, there are rats, but if they chewed wires and they were touching, I would see the short on the ohm meter. Link to comment Share on other sites More sharing options...
Tennessee williams Posted December 20, 2020 Share Posted December 20, 2020 Well. That IS weird. Sure there's no gfci outlet snuck in that circuit? Link to comment Share on other sites More sharing options...
Cholla Posted December 20, 2020 Share Posted December 20, 2020 Regular ohm meters don't always show a short/ground and they are usually powered by a 9 volt battery or less. Use a megohm meter. The units I use generate about 1000 volts dc which can show a breakdown in insulation while a regular meter will not. Link to comment Share on other sites More sharing options...
John Kloehr Posted December 20, 2020 Author Share Posted December 20, 2020 There are three GFCI outlets on the circuit that I have found. But Google chi did not find any evidence of GFCI outlets blowing breakers. The (2-prong) neon lamp was plugged into one of them. I have plenty of instances of bad GFCI outlets not working/tripping and also killing downstream outlets, but never an instance of a bad GFCI blowing a panel breaker. Link to comment Share on other sites More sharing options...
John Kloehr Posted December 20, 2020 Author Share Posted December 20, 2020 4 minutes ago, Cholla said: Regular ohm meters don't always show a short/ground and they are usually powered by a 9 volt battery or less. Use a megohm meter. The units I use generate about 1000 volts dc which can show a breakdown in insulation while a regular meter will not. Hmmm... Hi Pot test for an arc? Back in a minute with an edit. On edit: At 120V, I can't see a sustained arc, at 220V it seems to be possible. Will sleep on that but it would require two circuits on opposite legs to get close enough to each other to create an arc. Then assuming one breaker is quicker than the other, that one would trip. Link to comment Share on other sites More sharing options...
Cholla Posted December 20, 2020 Share Posted December 20, 2020 4 minutes ago, John Kloehr said: There are three GFCI outlets on the circuit that I have found. But Google chi did not find any evidence of GFCI outlets blowing breakers. The (2-prong) neon lamp was plugged into one of them. I have plenty of instances of bad GFCI outlets not working/tripping and also killing downstream outlets, but never an instance of a bad GFCI blowing a panel breaker. Don't use the megger on a wire still attached to the breaker in the panel. I have had GFCI receptacles blow circuit breakers. The best thing to do is start breaking the circuit down until the breaker trips stops. Pull the GFCI receptacle out and isolate the wires. See if the tripping stops. Link to comment Share on other sites More sharing options...
John Kloehr Posted December 20, 2020 Author Share Posted December 20, 2020 15 minutes ago, Cholla said: Don't use the megger on a wire still attached to the breaker in the panel. I have had GFCI receptacles blow circuit breakers. The best thing to do is start breaking the circuit down until the breaker trips stops. Pull the GFCI receptacle out and isolate the wires. See if the tripping stops. Breaker off, wire removed from breaker, confirmed no voltage on wire prior to testing ohms. I'll pull the wires off the GFCIs tomorrow and update then. Still open to other ideas, never had a popping breaker like this in the past without a dead short in the house wiring. Link to comment Share on other sites More sharing options...
Sedalia Dave Posted December 21, 2020 Share Posted December 21, 2020 Time to break down the circuit and begin isolating it. Can you access the attic so that you can physically map how the wiring goes from outlet to outlet? If you have a circuit hound it is a lot easier. Link to comment Share on other sites More sharing options...
Pat Riot Posted December 21, 2020 Share Posted December 21, 2020 I had a faulty GFCI give me fits years ago in the same scenario. Problem was that GFCI shouldn’t have been in the circuit it was affecting so I passed it by during troubleshooting. I am pretty sure a drunk wired that particular house. Link to comment Share on other sites More sharing options...
Tennessee williams Posted December 21, 2020 Share Posted December 21, 2020 1 hour ago, John Kloehr said: There are three GFCI outlets on the circuit that I have found. But Google chi did not find any evidence of GFCI outlets blowing breakers. The (2-prong) neon lamp was plugged into one of them. I have plenty of instances of bad GFCI outlets not working/tripping and also killing downstream outlets, but never an instance of a bad GFCI blowing a panel breaker. They can do it. Had a beaker a few months ago kept tripping. Stopped after replacing the bad gfci. It looked like it had gotten hot... Link to comment Share on other sites More sharing options...
Abilene Slim SASS 81783 Posted December 21, 2020 Share Posted December 21, 2020 Pull the covers and visually inspect all the outlets & connections on that circuit. Then pull the panel cover and visually inspect the breaker connections. Sometimes you find fried connection that shorts intermittently. I’ve found those at an outlet and a breaker. Link to comment Share on other sites More sharing options...
Dirty Dan Dawkins Posted December 21, 2020 Share Posted December 21, 2020 Sounds like a ground fault of some sort. Read for continuity from hot to ground. This will read through the ground to neutral bond at the main disconnect in the event there is a ground to neutral fault. You have to determine if it’s a ground fault or ground to neutral fault. If you turn the breaker off, disconnect the circuits neutral from the neutral bar and disconnect the equipment grounding conductor from the ground bar, all circuit conductors are then isolated for readings. I never go to such lengths. Too often I find ground faults where a bare ground and a hot wire makes contact in receptacle and switch boxes. I do service work at a lot of older apartments. Improperly mounted devices that spring in and out of the wall when plugging in, or the practice of back-stabbing devices are the culprit 90+% of the time. Now and then, I find it in the panel, but super rare. I have found a lot of ground faults from where whoever stripped the Romex cut cross ways with a razor knife and cut into and exposed the conductors, leading to a fault. Here’s a simple way using logic. Start by opening the receptacle used to vacuum. It could be reasoned the load of the vacuum brought forth a deficiency in the circuit, somewhere. Start where it plugged in. If you dont see anything try to logically reason how the circuit may be routed based on what devices you can reason are connected to it and work back to the breaker. If you can deduce half way point, you could open another receptacle box at that point, break the circuit. Try the breaker again to figure a direction to go. It’s a back and forth way of trouble shooting but I usually find faults this way fairly quick. 20-30 minutes tops unless i have to move a lot of furniture After working these apartments all these years, it’s funny all units are wired typically wired the exact same, but others buildings in the complex I have found will be wired different indicating a different crew of men. Link to comment Share on other sites More sharing options...
Kid Rich Posted December 21, 2020 Share Posted December 21, 2020 We had a gcfi that would trip occasionally. It finally got to the point it would not work at all. Traced the circuit back and found a receptacle that the wire had never been tightened correctly. kR Link to comment Share on other sites More sharing options...
John Kloehr Posted December 21, 2020 Author Share Posted December 21, 2020 Thanks for the encouragement to keep looking. The one where I used the vacuum was fine, and was at the end of the string. Or perhaps one of several ends. Split the "distance" (number of outlets/lights on the circuit by distance to the breaker box) and opened up a GFCI outlet in a bathroom: Opened up all boxes in the area, no other burned wiring in those. Looks like when the box was wired, one of the black wires had a nick next to the crimp. That failed slowly, heating everything up. It somehow did arc to the neutral crimp. I could smell it as soon as I removed the cover plate. Removed the plug and cut out a bunch of burned wire and the crimps. Used fresh wire nuts on the remaining stubs. Off to buy a blank plate as I have never used that plug. Not exactly a code compliant repair, but everything else works again. I'll watch for problems and sniff for smells for a while; at some point I will either need to fix this right or bulldoze the house. Kind of favor the bulldozer, and be cheaper and easier in the long run. Link to comment Share on other sites More sharing options...
Dirty Dan Dawkins Posted December 21, 2020 Share Posted December 21, 2020 14 minutes ago, John Kloehr said: Thanks for the encouragement to keep looking. The one where I used the vacuum was fine, and was at the end of the string. Or perhaps one of several ends. Split the "distance" (number of outlets/lights on the circuit by distance to the breaker box) and opened up a GFCI outlet in a bathroom: Opened up all boxes in the area, no other burned wiring in those. Looks like when the box was wired, one of the black wires had a nick next to the crimp. That failed slowly, heating everything up. It somehow did arc to the neutral crimp. I could smell it as soon as I removed the cover plate. Removed the plug and cut out a bunch of burned wire and the crimps. Used fresh wire nuts on the remaining stubs. Off to buy a blank plate as I have never used that plug. Not exactly a code compliant repair, but everything else works again. I'll watch for problems and sniff for smells for a while; at some point I will either need to fix this right or bulldoze the house. Kind of favor the bulldozer, and be cheaper and easier in the long run. This is a typical crimper an electrician uses to crimp grounds with. https://www.homedepot.com/p/Klein-Tools-9-1-2-in-Crimping-Tool-1005SEN/100352095 The cutting portion of the tool extends past the crimp portion of the tool. If you crimp tight into the box it is very easy to accidentally cut into an adjacent conductor. I learned to always, where possibly, have enough wire outside the box to crimp outside of the box. The NEC itself states 6" conductor length in the box. Of course most guys cut those solid grounds off pretty short, twisted them together and put a crimp sleeve on them. Those bulky GFCI's make it tough fitting everything in, they take up so much room. Leviton makes a low profile GFCI. Link to comment Share on other sites More sharing options...
Marshal Hangtree Posted December 21, 2020 Share Posted December 21, 2020 36 minutes ago, John Kloehr said: I'm betting your problem is the wall paper. Link to comment Share on other sites More sharing options...
Eyesa Horg Posted December 21, 2020 Share Posted December 21, 2020 Looks like you found that in the nick of time, no pun intended! Link to comment Share on other sites More sharing options...
Sedalia Dave Posted December 21, 2020 Share Posted December 21, 2020 You have discovered the remnants of a High resistance Arc. I experienced my first one a couple of years ago. Hooking up the ice maker on the garage fridge and when i pulled it out away from the wall noticed that the cover plate and outlet had scorched marks on them. Secured the power and opened the box only to discover that the outlet was badly melted inside the box. Had to replace the outlet, box and wiring in the wall. I'm thankful that it didn't burn the house down. Link to comment Share on other sites More sharing options...
Three Foot Johnson Posted December 21, 2020 Share Posted December 21, 2020 I had a similar problem with a kitchen outlet 'bout five years back - this is what happens when an old house is wired with only one kitchen circuit PLUS a living room light on the same 20 amp breaker. Link to comment Share on other sites More sharing options...
John Kloehr Posted December 21, 2020 Author Share Posted December 21, 2020 1 hour ago, Sedalia Dave said: You have discovered the remnants of a High resistance Arc. I experienced my first one a couple of years ago. Hooking up the ice maker on the garage fridge and when i pulled it out away from the wall noticed that the cover plate and outlet had scorched marks on them. Secured the power and opened the box only to discover that the outlet was badly melted inside the box. Had to replace the outlet, box and wiring in the wall. I'm thankful that it didn't burn the house down. It goes along with my thinking of a HiPot test. The distances in my case had to be "just perfect" to get a short/arc at 120V. Typically, arcs are not sustainable until about 400 V in terms of jumping a gap. In this case, repeated applications of heat worked to melt through the tape around the neutral crimp (and no tape on the hot crimp!). Until it got to the point that things got close enough to spark. In the last week, also added a heater to the RV and a couple other smaller loads to the circuits beyond the arc point, so pushed it over the edge. I got a bit stumped since my ohm meter was not showing a short, but the distance between hot an neutral must have worked down to a just few thousandth of an inch. It is very important after crimping/nutting wires to still physically separate them in the box; these connections were touching with pressure. Link to comment Share on other sites More sharing options...
Four-Eyed Buck,SASS #14795 Posted December 21, 2020 Share Posted December 21, 2020 About a month ago, I replaced an eye on a light post. Thought I had the wire nuts tight, guess what happened when I stuffed everything back into the post...........yup, dead short. Three white wire bundle slipped loose. Had to be in front of the office,too! Link to comment Share on other sites More sharing options...
Sedalia Dave Posted December 22, 2020 Share Posted December 22, 2020 15 hours ago, Three Foot Johnson said: I had a similar problem with a kitchen outlet 'bout five years back - this is what happens when an old house is wired with only one kitchen circuit PLUS a living room light on the same 20 amp breaker. That is what my outlet looked like. Strange thing though is that the fridge was the only thing on that circuit. Link to comment Share on other sites More sharing options...
Three Foot Johnson Posted December 22, 2020 Share Posted December 22, 2020 A refrigerator is supposed to have its own dedicated circuit. Link to comment Share on other sites More sharing options...
Finagler 6853 Life Posted December 22, 2020 Share Posted December 22, 2020 I had a circuit of lights and outlets that didn't work at all. Finally took the GFCI outlet out and found that little red ants had tried to make a best in it and there were lumber of dead bodies in the outlet. This outlet was outside on the deck. Link to comment Share on other sites More sharing options...
Capt. James H. Callahan Posted December 22, 2020 Share Posted December 22, 2020 Hell's Bells! Thank Heaven the breaker kept doing its job! JHC Link to comment Share on other sites More sharing options...
Recommended Posts
Archived
This topic is now archived and is closed to further replies.